Multiple cabinet electrical question [RESOLVED]

Having multiple grobo cabinets (currently 3 and possibly increase to 5 in future) what amperage should the separate circuit be?

In a new house the first harvest was before the move and basement breaker would trip occasionally trying to prevent that. Having them on their own separate breaker in the new place, what amperage should it be?

3 Likes

@Gary
That’s cool you have 3 Grobos and plan on increasing to 5! Wow!

Looking at the brick power adapter it says the following:
Input: 2A
Output: 6.67A

So if I interpret that correctly that means each Grobo pulls 2A

3 Likes

Hey @Gary,

Our units don’t use a lot of amps, or draw a lot of high current that would flip the breaker. I’ve had 10 running at a time on a 15 amp breaker. Only when we would use a tool in the lab would it flip.

Cheers,
Stephen

7 Likes

Wow I feel like I should have realized that info was on the power packs…

2 Likes

This makes sense any added and it tripped thanks for the quick reply

4 Likes